Plate Girder Stiffeners, End Panel Design & Splices (IS 800:2007 Cl. 8.7 & Cl. 10.3)
In this chapter (4 topics)
On this page
- 1. Executive Summary & Code Hierarchy
- 2. Classification & Structural Function of Stiffeners
- 3. Intermediate Transverse Stiffeners: Rigidity, Outstand & Strut Design
- 3.1 Minimum Second Moment of Area Is (IS 800:2007 Cl. 8.7.2.4)
- 3.2 Outstand Limitations (Cl. 8.7.1.2)
- 3.3 Strut Column Buckling Check (Cl. 8.7.2.4)
- 3.4 Connection to Web (IS 800 Cl. 8.7.2.6)
- 4. Bearing and Load-Carrying Stiffeners (IS 800 Cl. 8.7.3 & Cl. 8.7.4)
- 4.1 Direct Bearing on Flange (Web Crippling Check)
- 4.2 Column Buckling Capacity of Bearing Stiffener
- 5. Longitudinal (Horizontal) Stiffeners (IS 800 Cl. 8.7.1)
- 5.1 First Longitudinal Stiffener (at 0.20 d)
- 5.2 Second Longitudinal Stiffener (at 0.50 d)
- 6. End Panel Boundary Architecture: Rigid vs Non-Rigid End Posts
- 6.1 Non-Rigid End Post (Simple Post-Critical)
- 6.2 Rigid End Post (Twin Stiffeners)
- 7. Plate Girder Splices: Flange & Web Joints
- 7.1 Flange Splice Design (IS 800 Cl. 10.3)
- 7.2 Web Splice Design (IS 800 Cl. 10.3)
- 7.3 Golden Practical Rule: Staggering of Splices
- 8. SVG Engineering Visualizations
- FIGURE STEEL-05-03A: Stiffener Systems & Strut Column Sections
- FIGURE STEEL-05-03B: Flange & Web Splice Detailing & Vector Mechanics
- 9. Complete Step-by-Step Mathematical Derivations
- Derivation 1: Minimum Second Moment of Area Is for Transverse Stiffeners
- Derivation 2: Polar Modulus & Resultant Bolt Force in Web Splice
- 10. Multi-Exam Comprehensive Solved Examples
- Example 1: Design of Intermediate Transverse Stiffeners & Strut Check (GATE CE / ESE Conventional)
- Example 2: Design of End Bearing Stiffener at Support
- Example 3: Flange and Web Splice Design
- 11. Exam Traps, Common Pitfalls & Practical Fabrication Rules
- Trap 1: Confusing Intermediate Stiffener Rigidity with Strength
- Trap 2: Neglecting the Web Strip in Stiffener Column Checks
- Trap 3: Position of Longitudinal Stiffeners
- Trap 4: Direct Bearing Contact Snip
- Trap 5: Aligning Flange and Web Splices
- 12. Official Exam Practice Questions
- Question 1 (GATE CE)
- Question 2 (UPSC ESE)
- Question 3 (SSC JE)
- Question 4 (State AE)
- Question 5 (UPSC ESE Conventional)
1. Executive Summary & Code Hierarchy
In deep welded plate girders where the web slenderness ratio exceeds the limits of unstiffened serviceability (), the web plate cannot resist modern heavy railway and highway bridge loadings without specialized secondary stabilizing elements called stiffeners. Stiffeners are structural plates, angles, or rolled sections welded or bolted to the web plate to prevent out-of-plane buckling, ensure load dispersion, anchor post-buckling tension fields, and preserve cross-sectional geometry.
The design of plate girder stiffeners and field splices is governed by strict statutory specifications:
- IS 800:2007 (Section 8.7 & Section 10.3): Indian Standard General Construction in Steel — Code of Practice (Third Revision).
- IRC:24-2010: Standard Specifications and Code of Practice for Road Bridges — Steel Road Bridges.
- IRS (Indian Railway Standard) Steel Bridge Code: Mandating dynamic impact factors and fatigue life checks.
- Eurocode 3 (EN 1993-1-5): Plated structural elements.
- AISC 360-16 (Chapter G & Chapter J): Specification for Structural Steel Buildings.
In addition to stiffener detailing, long-span plate girders (typically exceeding ) cannot be transported from steel fabrication yards to the construction site in single pieces due to transportation clearances and vehicular payload limits. Consequently, they require field splices for both flanges and webs. Splicing high-capacity bridge girders demands rigorous limit-state detailing: flange splices must transmit massive tensile/compressive chord forces across joint gaps, while web splices must resist concurrent vertical shear and bending moment without slipping or overstressing fasteners.
┌───────────────────────────────────────────────────────────────────────────────────┐
│ STIFFENER HIERARCHY (IS 800:2007 Cl. 8.7) │
├───────────────────────────────────────────────────────────────────────────────────┤
│ 1. Intermediate Transverse Stiffeners (Cl. 8.7.2): │
│ - Prevent shear buckling by subdividing web into panels of aspect ratio c/d. │
│ - Act as compression struts anchoring post-buckling Tension Field Action (TFA).│
│ │
│ 2. Bearing / Load-Carrying Stiffeners (Cl. 8.7.3 & 8.7.4): │
│ - Prevent web crippling (local crushing) and web buckling at supports/loads. │
│ - Ground to direct bearing contact against flanges; designed as columns. │
│ │
│ 3. Longitudinal (Horizontal) Stiffeners (Cl. 8.7.1): │
│ - 1st Stiffener at 0.20 d from compression flange (prevents bending buckling). │
│ - 2nd Stiffener at Neutral Axis (0.50 d) (mandatory when d/tw > 400ε). │
│ │
│ 4. End Panel Anchors: Rigid End Post vs Non-Rigid End Post (Cl. 8.5.3). │
└───────────────────────────────────────────────────────────────────────────────────┘
2. Classification & Structural Function of Stiffeners
Stiffeners in plate girders are classified by their physical orientation and structural role:
-
Intermediate Transverse Web Stiffeners (Vertical):
- Welded perpendicular to the girder axis across the full or partial depth of the web.
- They divide a long flexible web into short panels of width , drastically increasing the critical elastic shear buckling stress by raising the shear buckling coefficient .
- When Tension Field Action develops, they act as vertical compression struts in an equivalent Pratt truss, resisting vertical force components .
-
Load-Carrying and Bearing Stiffeners (Support / Concentrated Load):
- Positioned at locations of concentrated loads and reactions (e.g., bridge abutments, pier bearings, column junctions).
- They transfer heavy vertical forces directly into the support without permitting localized web crushing (web crippling) or column buckling of the unstiffened web plate.
-
Longitudinal (Horizontal) Stiffeners:
- Welded parallel to the longitudinal axis of the girder on the web.
- When a deep girder bends, the web above the neutral axis is subjected to compressive bending stresses . If , this zone will buckle elastically out of plane.
- Placing a longitudinal stiffener at from the compression flange creates a nodal line of zero out-of-plane displacement, effectively increasing the bending buckling strength by over .
-
Torsional / End Diagonal Stiffeners:
- Provided at bearings to prevent the girder from twisting or rolling over at the supports (providing torsional restraint as required by IS 800 Table 15).
3. Intermediate Transverse Stiffeners: Rigidity, Outstand & Strut Design
3.1 Minimum Second Moment of Area (IS 800:2007 Cl. 8.7.2.4)
To ensure that an intermediate transverse stiffener remains rigid and creates a true nodal line during web buckling, it must possess a minimum moment of inertia about the centerline of the web:
where:
- is the clear depth of the web between flanges.
- is the web thickness.
- is the spacing between adjacent transverse stiffeners.
Note on calculation: For a pair of flat stiffeners of outstand and thickness welded symmetrically on both sides of the web, the total width across the web is . The moment of inertia about the center of the web is:
3.2 Outstand Limitations (Cl. 8.7.1.2)
To prevent local torsional buckling of the stiffener plate itself before it mobilizes its full strength:
- For flat stiffeners (unstiffened outstand):
- For angle or tee sections (stiffened outstand):
where . For Fe 410 steel (), .
3.3 Strut Column Buckling Check (Cl. 8.7.2.4)
When intermediate stiffeners are not subjected to concentrated external loads, they must still be checked as an axial compression member (strut) if Tension Field Action is mobilized in the web panels.
-
Effective Column Section:
- The effective column consists of the stiffener plates plus an effective strip of web of width ( on each side of the stiffener centerline, or total if at an edge).
-
Effective Length:
(The flanges provide rotational and lateral restraint at the top and bottom).
-
Design Compressive Strength :
The design compressive stress is obtained from Buckling Curve c () per IS 800 Cl. 7.1.2.1:
-
Design Axial Force from Tension Field Action:
where is the maximum design shear force in the adjacent panels, and is the simple post-critical shear buckling strength. The stiffener is safe if:
3.4 Connection to Web (IS 800 Cl. 8.7.2.6)
Intermediate transverse stiffeners must be connected to the web by welds designed to resist a minimum shear force per unit length:
where and are in mm. Furthermore, transverse stiffeners not subjected to external loads may stop short of the tension flange by a distance not exceeding to prevent fatigue cracking of the tension flange under cyclic loading.
4. Bearing and Load-Carrying Stiffeners (IS 800 Cl. 8.7.3 & Cl. 8.7.4)
At supports or under heavy concentrated wheel loads (e.g., gantry cranes), the web is subjected to massive compressive stresses that can cause instantaneous crushing (web crippling) or out-of-plane buckling.
4.1 Direct Bearing on Flange (Web Crippling Check)
Bearing stiffeners must be fitted tightly against the loaded flange (ground to direct bearing or connected by full-penetration butt welds). The design bearing capacity of the stiffener alone against the flange is given by:
where:
- is the net contact bearing area between the stiffener and the flange plate.
- To clear the continuous web-to-flange fillet welds, the inner corner of the stiffener plate must be snipped (coped) by a dimension .
- For a pair of bearing stiffeners:
4.2 Column Buckling Capacity of Bearing Stiffener
The assembly of bearing stiffeners and the web plate acts as a vertical compression member.
- Effective Web Width: A width of web equal to ( on either side of the stiffener, or total at the end of a cantilever or end support).
- Effective Length: (when flanges are restrained against lateral translation and rotation).
- Buckling Capacity: Sized to satisfy: where is the factored support reaction.
5. Longitudinal (Horizontal) Stiffeners (IS 800 Cl. 8.7.1)
Longitudinal stiffeners are required when the web slenderness is high:
COMPRESSION FLANGE
══════════════════════════════════════════════════════════
│ ▲
│ │ 0.20 d ──► 1st LONGITUDINAL STIFFENER (I_s1 ≥ 4 c tw³)
│ ▼ (At centroid of flexural compressive stress)
│
│ 2nd LONGITUDINAL STIFFENER (I_s2 ≥ c tw³)
│ ─── 0.50 d ──► (At Neutral Axis - prevents shear buckling)
│
│
│
══════════════════════════════════════════════════════════
TENSION FLANGE
5.1 First Longitudinal Stiffener (at )
- Location: Placed at a distance of from the inner face of the compression flange.
- Structural Rationale: Under pure bending, compressive normal stress varies linearly from zero at the neutral axis () to maximum at the top edge (). The resultant compressive force acts at one-third depth of the compression zone, which corresponds precisely to: Placing the stiffener at divides the compression zone into two panels: and . The sub-panel has a very small depth, preventing elastic flexural buckling.
- Minimum Moment of Inertia (IS 800 Cl. 8.7.1.3):
5.2 Second Longitudinal Stiffener (at )
- Location: Placed at the neutral axis ().
- Structural Rationale: Provides additional shear buckling resistance and prevents asymmetrical lateral buckling when approaches the statutory maximum ceiling of .
- Minimum Moment of Inertia (IS 800 Cl. 8.7.1.4):
6. End Panel Boundary Architecture: Rigid vs Non-Rigid End Posts
Under IS 800:2007 Cl. 8.5.3, the end panel of a plate girder designed with Tension Field Action must anchor the horizontal component of the diagonal membrane tension :
6.1 Non-Rigid End Post (Simple Post-Critical)
- Consists of a single vertical bearing stiffener placed at the centerline of the support bearing.
- The single stiffener has zero flexural rigidity in the longitudinal plane of the girder and cannot resist .
- Consequently, the end panel cannot develop Tension Field Action.
- The end panel must be designed using the Simple Post-Critical Method (). Since maximum shear occurs at the support, the designer must either:
- Reduce stiffener spacing near the support (e.g., ) to raise and .
- Increase the web plate thickness in the end panel.
6.2 Rigid End Post (Twin Stiffeners)
- Fabricated using two vertical stiffeners spaced at a distance apart, connected by the web plate to form a closed vertical box or I-beam.
- The rigid end post spans vertically as a beam between the top and bottom flanges (span length ).
- It resists the horizontal pull through vertical beam bending.
- The design bending moment in the rigid end post is:
- Providing a rigid end post allows the end panel to develop full Tension Field Action (), avoiding web thickening or congested stiffeners.
7. Plate Girder Splices: Flange & Web Joints
When girder spans exceed transportable lengths (), field splices are required.
FLANGE SPLICE
┌─────────────────────┐ Outer Splice Plate
▼ ▼
════════════════════ ════════════════════
════════════════════ ════════════════════ Main Flange
▲ ▲
└─────────────────────┘ Inner Splice Plates (Straddling web)
│ Joint Gap (5-10 mm)
▼
──────────────────── ────────────────────
│ │ │ │
│ │ │ │ WEB SPLICE:
│ ┌───────────────────────┐ │ Double cover plates
│ │ o o o │ o o │ │ resisting Vu & Mw
│ │ o o o │ o o │ │
│ │ o o o │ o o │ │
│ └───────────────────────┘ │
│ │ │ │
──────────────────── ────────────────────
7.1 Flange Splice Design (IS 800 Cl. 10.3)
-
Design Force : Standard code practice mandates that the flange splice be designed to transmit the full plastic tensile/compressive capacity of the flange:
(Alternatively, the actual design force may be used, provided it is not less than of the full strength).
-
Splice Plates:
- An outer splice cover plate placed on the exterior face ().
- Two inner splice plates placed on the interior face, straddling the web on each side of the fillet weld.
- Total cross-sectional area:
-
Fastener Design (Double Shear):
- High-Strength Friction Grip (HSFG Class 8.8 or 10.9) bolts are preferred to prevent slip.
- Number of bolts required on each side of the joint: where is the double-shear capacity per bolt.
7.2 Web Splice Design (IS 800 Cl. 10.3)
The web splice is placed at a section of low bending moment (e.g., quarter-span) and consists of two cover plates sandwiching the web plate ().
-
Applied Design Forces:
- Factored vertical shear: .
- Bending moment carried by the web:
-
Bolt Force Distribution (Vector Analysis):
- On each side of the joint, an array of bolts in vertical rows is provided.
- Direct vertical shear force per bolt:
- Torsional moment shear force on extreme bolt: acting perpendicular to the radius vector .
- Combined Resultant Shear Force on Critical Bolt: where is the angle between the vectors and .
7.3 Golden Practical Rule: Staggering of Splices
NEVER SPLICE FLANGES AND WEBS AT THE SAME CROSS-SECTION. Splicing both flanges and the web in the same vertical plane creates a continuous weak discontinuity across the entire girder. Flange splices and web splices must be staggered longitudinally by at least (or separated by a full panel width).
8. SVG Engineering Visualizations
FIGURE STEEL-05-03A: Stiffener Systems & Strut Column Sections
The following technical drawing details the elevation of a deep plate girder showing intermediate, longitudinal, and bearing stiffeners, alongside the plan views of effective column strut sections.
FIGURE STEEL-05-03B: Flange & Web Splice Detailing & Vector Mechanics
The following engineering schematic illustrates the detailing of bolted flange and web splices, force transfer across cover plates, and the resultant shear force vector acting on the critical corner bolt.
9. Complete Step-by-Step Mathematical Derivations
Derivation 1: Minimum Second Moment of Area for Transverse Stiffeners
Consider an infinitely long plate of width simply supported along its longitudinal edges (flanges), subjected to shear stress . When transverse stiffeners are placed at spacing , they divide the plate into panels of aspect ratio .
-
For the stiffeners to enforce a pure nodal line ( along the stiffener axis) during out-of-plane buckling, the flexural rigidity of the stiffener must exceed the critical threshold derived by Timoshenko and Bryan:
where is the plate flexural rigidity.
-
Empirical and theoretical energy solutions establish that for :
Substituting with and introducing a factor of safety of for limit-state compliance:
-
For wide panels where , buckling initiates in higher order harmonics between stiffeners, scaling inversely with :
Derivation 2: Polar Modulus & Resultant Bolt Force in Web Splice
Consider a web splice connection with bolts subjected to a factored bending moment and factored vertical shear . The centroid of the bolt group is located at .
-
The vertical shear load is distributed uniformly among all bolts:
-
The moment causes each bolt located at to exert a restoring couple. The shear force on bolt due to moment is proportional to its distance from the centroid :
The total resisting moment is:
where is the polar moment of inertia of the bolt group. The maximum force occurs on the bolt with maximum radius :
-
Vector acts perpendicular to the radius vector . The angle between the downward vertical vector and is:
The resultant shear force on the extreme critical bolt is obtained via the law of cosines:
10. Multi-Exam Comprehensive Solved Examples
Example 1: Design of Intermediate Transverse Stiffeners & Strut Check (GATE CE / ESE Conventional)
Problem Statement: A plate girder has a clear web depth and web thickness (). Intermediate transverse stiffeners are provided at (). At the section, the design shear force is and the simple post-critical shear capacity is .
- Determine the minimum required moment of inertia per IS 800:2007.
- Select a suitable pair of flat stiffeners and verify the outstand limit.
- Check the stiffener as an axial strut under post-buckling Tension Field Action force .
Solution:
Step 1: Minimum Second Moment of Area
- Aspect ratio:
- Required (IS 800 Cl. 8.7.2.4):
Step 2: Trial Stiffener Section & Outstand Check
- Try a pair of flat stiffeners welded on opposite sides of the web:
- Outstand width:
- Thickness:
- Outstand limit check (Cl. 8.7.1.2): Since , outstand is completely SAFE against local buckling.
- Total width across the web:
- Moment of inertia provided about the web centerline:
- Check rigidity:
Step 3: Strut Column Buckling Check under TFA Force
- Effective column section (pair of flats + web strip):
- Moment of inertia of effective section about web axis:
- Radius of gyration:
- Effective length:
- Slenderness ratio:
- Design compressive stress (Buckling Curve c, ):
- Euler stress:
- Non-dimensional slenderness:
- Design axial compressive strength:
- Axial force to resist from Tension Field Action (noting from Step 1 already incorporates ):
- Comparison:
Example 2: Design of End Bearing Stiffener at Support
Problem Statement: Design an end bearing stiffener for a plate girder supporting a factored reaction . Web plate is and flange plates are (). Check direct bearing, column buckling, and weld connection to the web.
Solution:
Step 1: Stiffener Geometry Selection
- Available width on either side of web:
- Adopt a pair of plates: , thickness .
- Provide a snip (chamfer) of to clear the web-to-flange fillet weld.
- Outstand check:
Step 2: Direct Flange Bearing Check (Cl. 8.7.4)
- Net bearing contact area:
- Design bearing capacity:
- Check:
Step 3: Column Buckling Check (Cl. 8.7.3)
- Effective section: 2 stiffener plates + web strip of .
- Total width across web: .
- Moment of inertia:
- Radius of gyration:
- Effective length:
- Slenderness:
- Per IS 800:2007 Clause 7.1.2.1, since , the stress reduction factor is capped at :
- Compressive capacity:
- Check:
Step 4: Weld Connecting Stiffeners to Web
- Total available weld length (4 continuous fillet runs):
- Shear stress per mm:
- Providing standard shop fillet weld ():
- Check:
Example 3: Flange and Web Splice Design
Problem Statement: A plate girder has a web of and flanges of (). A field splice is located where the factored bending moment is and factored shear is .
- Design the flange splice plates and determine the number of M24 Grade 8.8 bolts () for the full tensile capacity.
- Determine the portion of bending moment carried by the web .
Solution:
Step 1: Section Properties & Moment Distribution
- Moment of inertia of flanges:
- Moment of inertia of web:
- Total moment of inertia:
- Portion of moment carried by flanges:
- Portion of moment carried by web:
Step 2: Flange Splice Design (Full Plastic Flange Strength)
- Full plastic tensile/compressive strength of flange:
- Provide:
- Outer splice plate: ()
- Two inner splice plates: each ()
- Total splice plate area:
- Splice plate capacity:
- Bolts required on each side of the flange joint (M24 Gr 8.8 in double shear, ):
- Provide 12 bolts of M24 Grade 8.8 on each side of the joint (arranged in 3 rows of 4 bolts).
Step 3: Web Splice Configuration
- Provide two web splice plates (one on each side of web):
- Height , thickness each ().
- Designed to resist concurrent shear and web moment .
11. Exam Traps, Common Pitfalls & Practical Fabrication Rules
Trap 1: Confusing Intermediate Stiffener Rigidity with Strength
- The Trap: Designing intermediate stiffeners purely for axial load capacity without checking the minimum moment of inertia .
- The Reality: If , the stiffener deflects out of plane alongside the buckled web, failing to create a nodal boundary! The condition ( or ) is mandatory.
Trap 2: Neglecting the Web Strip in Stiffener Column Checks
- In both bearing stiffeners and intermediate struts, the effective compression member is NOT just the stiffener plates alone. It is a cruciform/tee section comprising the stiffeners plus an effective web strip of ( on each side of the stiffener). Neglecting this strip severely underestimates the column buckling capacity.
Trap 3: Position of Longitudinal Stiffeners
- Frequent Exam Error: Stating that the first longitudinal stiffener is placed at or .
- Standard Specification: IS 800 Cl. 8.7.1 explicitly mandates the first longitudinal stiffener at from the compression flange, and the second at (Neutral Axis).
Trap 4: Direct Bearing Contact Snip
- Bearing stiffeners must be tightly fitted against the flange. However, if the corner is not snipped (coped by ), the stiffener rides on the bead of the web-to-flange fillet weld, creating an eccentric point load that induces severe localized weld cracking.
Trap 5: Aligning Flange and Web Splices
- Catastrophic Site Failure: Placing flange and web splices in the same vertical cross-section creates an unbraced plane of weakness. Always stagger splices by a minimum of .
12. Official Exam Practice Questions
Question 1 (GATE CE)
According to IS 800:2007, an intermediate transverse stiffener in a plate girder of web depth and web thickness spaced at must have a minimum second moment of area not less than:
- (A)
- (B)
- (C)
- (D)
Detailed Solution:
- Check aspect ratio:
- Since :
- Correct Answer: (A)
Question 2 (UPSC ESE)
In a welded plate girder, the first horizontal (longitudinal) stiffener is provided at a distance from the compression flange equal to:
- (A)
- (B)
- (C)
- (D)
Detailed Solution:
- The first longitudinal stiffener is provided at from the compression flange to arrest flexural compressive buckling in the web.
- Correct Answer: (B)
Question 3 (SSC JE)
The outstand of an unstiffened flat transverse stiffener of thickness fabricated from Fe 410 steel shall not exceed:
- (A)
- (B)
- (C)
- (D)
Detailed Solution:
- Per IS 800:2007 Cl. 8.7.1.2, the outstand of an unstiffened flat stiffener shall not exceed . For Fe 410, .
- Correct Answer: (B)
Question 4 (State AE)
When checking an intermediate transverse stiffener as an axial compression member under tension field action, the effective length is taken as:
- (A)
- (B)
- (C)
- (D)
Detailed Solution:
- Per IS 800:2007 Cl. 8.7.2.4, the effective length of the stiffener strut is taken as due to the rotational and lateral restraint provided by the heavy flanges.
- Correct Answer: (C)
Question 5 (UPSC ESE Conventional)
Discuss the functions of bearing stiffeners in a plate girder. Explain why bearing stiffeners are designed for both direct flange bearing and column buckling, and state the effective width of web assumed to act with the stiffener.
Detailed Solution:
- Primary Functions:
- To transfer heavy support reactions or concentrated loads safely into the web without local crushing (web crippling).
- To act as a vertical column preventing out-of-plane buckling of the web plate at reaction points.
- To provide torsional end restraint to the girder against twisting at the bearings.
- Dual Design Checks:
- Direct Bearing Check: Stiffener ends are machined/ground to bear directly against the loaded flange. The contact area transfers the load directly across the interface. The capacity is checked as to avoid localized yielding of the stiffener toes.
- Column Buckling Check: The load is then dispersed into the web plate. The combined stiffener-web assembly must have sufficient flexural rigidity about the web axis to act as a compression strut of length under Buckling Curve c without buckling out of plane.
- Effective Web Strip:
- The code specifies an effective web strip of ( on either side of the stiffener centerline, or total at an end support) acting compositely with the stiffener plates.