RCC-05-01 Chapter 05 · Design of Slabs

Design of One-Way Slabs

Subject
Reinforced Concrete Structures (notes/reinforced_cement_concrete)
Chapter
Chapter 05: Design of Slabs
Applicable Codes
IS 456:2000 (Clauses 22.2, 24.1, 26.2.1, 26.3.3, 26.5.2, 40.2.1.1, Table 12, Table 13, Table 19), SP 16, SP 34
Exam Target
GATE CE, UPSC ESE, SSC JE, State AE/JE, RRB JE
In this chapter (3 topics)
On this page
  1. 1. Introduction & Structural Mechanics of One-Way Slabs
  2. 1.1 Fundamental Criteria for One-Way Action (Clause 24.1)
  3. 1.2 Mathematical Mechanics: Load Distribution via Grillage Analogy
  4. 2. Effective Span Provisions (Clause 22.2)
  5. 3. Flexural Design Formulation (Unit Strip Method)
  6. 3.1 Limiting Depth of Section (dreq)
  7. 3.2 Main Tension Reinforcement (Ast)
  8. 4. Reinforcement Rules & Codal Detailing Mandates
  9. 4.1 Minimum Reinforcement (Clause 26.5.2.1)
  10. 4.2 Maximum Bar Diameter (Clause 26.5.2.2)
  11. 4.3 Maximum Clear Spacing of Reinforcement (Clause 26.3.3b)
  12. 4.4 Purpose of Distribution Reinforcement
  13. 5. Shear Resistance in One-Way Slabs (Clause 40.2.1.1)
  14. 6. Continuous One-Way Slabs & Bending Moment Coefficients (Tables 12 & 13)
  15. 6.1 Bending Moment Coefficients (Table 12)
  16. 6.2 Shear Force Coefficients (Table 13)
  17. 7. Engineering Diagrams & Detailing Anatomy
  18. Diagram 1: One-Way Slab Behavior & 1-Meter Design Strip Idealization
  19. Diagram 2: One-Way Slab Reinforcement Detailing & Curtailment Rules
  20. 8. Step-by-Step Design Procedure for One-Way Slabs
  21. 9. Pre-Calculated Solved Numerical Examples
  22. Example 1: Comprehensive Design of a Simply Supported One-Way Slab
  23. Example 2: Continuous One-Way Slab Analysis per IS 456 Table 12 & Table 13
  24. Example 3: Cantilever Chhajja / Balcony Slab Design & Detailing
  25. 10. Engineering Misconceptions & Site Detailing Pitfalls
  26. 11. Comparative Analysis: One-Way Slabs vs Two-Way Slabs
  27. 12. Competitive Exam Traps & High-Yield Takeaways
  28. 13. Practice Questions & Exercises
  29. Question 1 (GATE CE)
  30. Question 2 (UPSC ESE)
  31. Question 3 (SSC JE)

1. Introduction & Structural Mechanics of One-Way Slabs

A slab is a two-dimensional planar structural element having an overall depth (DD) that is very small compared to its span dimensions (LxL_x and LyL_y). Slabs serve as structural floors and roofs, transmitting transverse gravity and imposed surface loads directly to supporting beams, walls, or columns.

                           CLASSIFICATION BY ASPECT RATIO
                                         │
        ┌────────────────────────────────┴────────────────────────────────┐
        ▼                                                                 ▼
   ONE-WAY SLAB (Ly / Lx > 2.0)                                     TWO-WAY SLAB (Ly / Lx ≤ 2.0)
 ┌───────────────────────────────────┐                             ┌───────────────────────────────────┐
 │ • Bends primarily along short span│                             │ • Bends significantly along both  │
 │ • Cylindrical surface curvature   │                             │   orthogonal directions           │
 │ • Load path: >90% to long beams   │                             │ • Dishing / saucer curvature      │
 │ • Designed as 1-m wide strip beam │                             │ • Load shared between both pairs  │
 │ • Transverse steel: distribution  │                             │   of supporting beams/walls       │
 └───────────────────────────────────┘                             └───────────────────────────────────┘

1.1 Fundamental Criteria for One-Way Action (Clause 24.1)

A slab behaves and is designed as a one-way slab under either of two conditions:

  1. Aspect Ratio Threshold: When the slab is supported along all four edges by beams or masonry walls, but the ratio of the longer span (LyL_y) to the shorter span (LxL_x) exceeds 2.0: LyLx>2.0\frac{L_y}{L_x} > 2.0
  2. Two Opposite Edges Supported: Regardless of the aspect ratio, whenever a slab is supported on only two opposite parallel edges (with the other two edges entirely unsupported or free), all applied loads are constrained to span between those two supports.

1.2 Mathematical Mechanics: Load Distribution via Grillage Analogy

Consider an elastic slab carrying a uniformly distributed surface load ww. If modeled as two intersecting central orthogonal strips of unit width (Strip X of length LxL_x and Strip Y of length LyL_y) carrying portions wxw_x and wyw_y respectively (w=wx+wyw = w_x + w_y):

Δx=5wxLx4384EI,Δy=5wyLy4384EI\Delta_x = \frac{5 w_x L_x^4}{384 E I}, \quad \Delta_y = \frac{5 w_y L_y^4}{384 E I}

Equating deflections at the central intersection point (Δx=Δy\Delta_x = \Delta_y):

wxwy=(LyLx)4\frac{w_x}{w_y} = \left(\frac{L_y}{L_x}\right)^4

When Ly/Lx=2.0L_y / L_x = 2.0:

wxwy=24=16  ⟹  wx=1617w≈94.1%⋅w,wy=117w≈5.9%⋅w\frac{w_x}{w_y} = 2^4 = 16 \implies w_x = \frac{16}{17} w \approx 94.1\% \cdot w, \quad w_y = \frac{1}{17} w \approx 5.9\% \cdot w

When Ly/Lx=3.0L_y / L_x = 3.0:

wxwy=34=81  ⟹  wx=8182w≈98.8%⋅w\frac{w_x}{w_y} = 3^4 = 81 \implies w_x = \frac{81}{82} w \approx 98.8\% \cdot w

Because more than 94%94\% of the total load is transferred along the shorter span LxL_x, the bending moment along the long direction is negligible. Consequently, the slab deforms into a cylindrical surface, and can be accurately designed as an independent beam of unit width (b=1000 mmb = 1000\text{ mm}) spanning across LxL_x.


2. Effective Span Provisions (Clause 22.2)

The design bending moments and shears depend upon the statutory effective span LeffL_{\text{eff}} specified in IS 456:2000 Clause 22.2:

┌───────────────────────────────┬────────────────────────────────────────────────────────────────────────┐
│ Support Condition             │ Statutory Effective Span Formula (L_eff)                               │
├───────────────────────────────┼────────────────────────────────────────────────────────────────────────┤
│ Simply Supported (Cl. 22.2a)  │ L_eff = min[ (L_0 + d),  (L_0 + w) ]                                   │
│                               │ Where L_0 = clear span, d = effective depth, w = support width.        │
├───────────────────────────────┼────────────────────────────────────────────────────────────────────────┤
│ Continuous: w < L_0 / 12      │ L_eff = min[ (L_0 + d),  (L_0 + w) ]                                   │
│ (Narrow Supports, Cl. 22.2b1) │ Same as simply supported condition.                                    │
├───────────────────────────────┼────────────────────────────────────────────────────────────────────────┤
│ Continuous: w ≥ L_0 / 12      │ L_eff = L_0  (for clear span between rigid wide supports)               │
│ (Wide Supports, Cl. 22.2b2)   │ Or center-to-center if w < 600 mm, whichever is smaller.               │
├───────────────────────────────┼────────────────────────────────────────────────────────────────────────┤
│ Cantilever: Built into Wall   │ L_eff = L_0 + d / 2                                                    │
│ (Cl. 22.2c)                   │                                                                        │
├───────────────────────────────┼────────────────────────────────────────────────────────────────────────┤
│ Cantilever: Monolithic / Beam │ L_eff = L_0 + w / 2                                                    │
│ Continuous into support       │ Where w is the width of the supporting beam or column.                 │
└───────────────────────────────┴────────────────────────────────────────────────────────────────────────┘

3. Flexural Design Formulation (Unit Strip Method)

3.1 Limiting Depth of Section (dreqd_{\text{req}})

For a 1-meter wide strip (b=1000 mmb = 1000\text{ mm}), the section is designed as a balanced or under-reinforced rectangular beam. The minimum effective depth to resist the factored bending moment MuM_u without compression reinforcement is:

Mu,lim⁡=Qlim⁡⋅fck⋅b⋅d2  ⟹  dmin,flexure=MuQlim⁡⋅fck⋅1000M_{u,\lim} = Q_{\lim} \cdot f_{ck} \cdot b \cdot d^2 \implies d_{\text{min,flexure}} = \sqrt{\frac{M_u}{Q_{\lim} \cdot f_{ck} \cdot 1000}}

Where Qlim⁡Q_{\lim} values per IS 456:2000 are:

  • Fe 250 (Mild Steel): Qlim⁡=0.148Q_{\lim} = 0.148 (xu,max⁡/d=0.53x_{u,\max} / d = 0.53)
  • Fe 415 (HYSD): Qlim⁡=0.138Q_{\lim} = 0.138 (xu,max⁡/d=0.48x_{u,\max} / d = 0.48)
  • Fe 500 (TMT): Qlim⁡=0.133Q_{\lim} = 0.133 (xu,max⁡/d=0.46x_{u,\max} / d = 0.46)

[!NOTE] In practical slab design, deflection criteria (serviceability) almost always governs the choice of overall thickness (D≈Span/25 to Span/32D \approx \text{Span} / 25 \text{ to } \text{Span} / 32). Hence, the provided depth dd is considerably larger than dmin,flexured_{\text{min,flexure}}, guaranteeing a significantly under-reinforced, highly ductile section (xu≪xu,lim⁡x_u \ll x_{u,\lim}).

3.2 Main Tension Reinforcement (AstA_{st})

Using the IS 456 quadratic stress block relation:

Mu=0.87fyAstd(1−Astfyb⋅d⋅fck)M_u = 0.87 f_y A_{st} d \left(1 - \frac{A_{st} f_y}{b \cdot d \cdot f_{ck}}\right)

Solving for required tensile area per 1-meter strip (b=1000 mmb = 1000\text{ mm}):

Ast=0.5fckfy[1−1−4.59Mufck⋅b⋅d2]⋅b⋅dA_{st} = \frac{0.5 f_{ck}}{f_y} \left[1 - \sqrt{1 - \frac{4.59 M_u}{f_{ck} \cdot b \cdot d^2}}\right] \cdot b \cdot d

Spacing ss of bars with diameter ϕ\phi (individual bar area ast=π4ϕ2a_{st} = \frac{\pi}{4} \phi^2):

s=1000⋅astAsts = \frac{1000 \cdot a_{st}}{A_{st}}

4. Reinforcement Rules & Codal Detailing Mandates

                          STATUTORY SLAB REINFORCEMENT RULES
                                          │
        ┌─────────────────────────────────┼─────────────────────────────────┐
        ▼                                 ▼                                 ▼
   MINIMUM STEEL (Ast,min)        MAXIMUM BAR DIAMETER            MAXIMUM BAR SPACING
 ┌─────────────────────────┐     ┌─────────────────────────┐     ┌─────────────────────────┐
 │ • Mild Steel (Fe 250):  │     │ • ϕ_max ≤ D / 8         │     │ • Main Steel:           │
 │   0.15% b·D             │     │   (Cl. 26.5.2.2)        │     │   s ≤ min(3d, 300 mm)   │
 │ • HYSD (Fe 415/500):    │     │ • Example: For D=120 mm,│     │ • Distribution Steel:   │
 │   0.12% b·D             │     │   ϕ ≤ 15 mm (use ≤12 mm)│     │   s ≤ min(5d, 450 mm)   │
 │   (Cl. 26.5.2.1)        │     │                         │     │   (Cl. 26.3.3b)         │
 └─────────────────────────┘     └─────────────────────────┘     └─────────────────────────┘

4.1 Minimum Reinforcement (Clause 26.5.2.1)

To prevent sudden brittle rupture upon initial concrete cracking and control shrinkage/temperature strains:

Ast,min⁡={0.0015⋅b⋅D=0.15%⋅bDfor Mild Steel (Fe 250)0.0012⋅b⋅D=0.12%⋅bDfor HYSD / TMT Bars (Fe 415, Fe 500)A_{st,\min} = \begin{cases} 0.0015 \cdot b \cdot D = 0.15\% \cdot b D & \text{for Mild Steel (Fe 250)} \\ 0.0012 \cdot b \cdot D = 0.12\% \cdot b D & \text{for HYSD / TMT Bars (Fe 415, Fe 500)} \end{cases}

Note: This minimum percentage applies to the gross total depth DD, not the effective depth dd.

4.2 Maximum Bar Diameter (Clause 26.5.2.2)

To maintain structural ductility and ensure adequate concrete surround:

ϕmax⁡≤D8\phi_{\max} \le \frac{D}{8}

Example: For a slab with D=100 mmD = 100\text{ mm}, the maximum allowable rebar diameter is 100/8=12.5 mm100 / 8 = 12.5\text{ mm} (use 10 mm10\text{ mm} or 12 mm12\text{ mm} bars).

4.3 Maximum Clear Spacing of Reinforcement (Clause 26.3.3b)

  1. Main Reinforcement (Short Span):
    The horizontal pitch / spacing of main tension bars must not exceed: smain,max⁡≤min⁡(3d,  300 mm)s_{\text{main},\max} \le \min(3d,\; 300\text{ mm})
  2. Distribution / Secondary Reinforcement (Long Direction):
    Distribution bars placed perpendicular to main steel must satisfy: sdist,max⁡≤min⁡(5d,  450 mm)s_{\text{dist},\max} \le \min(5d,\; 450\text{ mm})

4.4 Purpose of Distribution Reinforcement

Although structural analysis assumes zero moment along the long span LyL_y, distribution bars are mandatory in one-way slabs to:

  1. Resist tensile stresses induced by concrete shrinkage and daily temperature variations.
  2. Distribute concentrated point loads or wheel wheel patches laterally over a wider effective slab width (beffb_{\text{eff}} per IS 456 Clause 24.3.2).
  3. Hold the main bottom reinforcement securely in position during concrete pouring and vibratory compaction.

5. Shear Resistance in One-Way Slabs (Clause 40.2.1.1)

Shear is rarely critical in slabs under uniformly distributed loads because the slab thickness provided for deflection control yields very low nominal shear stresses:

  1. Nominal Shear Stress: τv=Vub⋅d=Vu1000⋅d\tau_v = \frac{V_u}{b \cdot d} = \frac{V_u}{1000 \cdot d}
  2. Permissible Shear Strength (k⋅τck \cdot \tau_c):
    Unlike beams, thin slabs benefit from multi-axial constraint and load dispersal. IS 456 Clause 40.2.1.1 enhances the design concrete shear strength τc\tau_c (from Table 19) by a depth modification factor kk: τc,slab=k⋅τc\tau_{c,\text{slab}} = k \cdot \tau_c
┌─────────────────────────┬───────┬───────┬───────┬───────┬───────┬───────┬────────────┐
│ Overall Depth D (mm)    │ ≤ 150 │  175  │  200  │  225  │  250  │  275  │ ≥ 300 mm   │
├─────────────────────────┼───────┼───────┼───────┼───────┼───────┼───────┼────────────┤
│ Slab Depth Factor (k)   │ 1.30  │ 1.25  │ 1.20  │ 1.15  │ 1.10  │ 1.05  │ 1.00       │
└─────────────────────────┴───────┴───────┴───────┴───────┴───────┴───────┴────────────┘

[!CRITICAL] Codal Mandate on Slab Shear Reinforcement:
In building slabs, shear stirrups are never provided. The cross-section must be sized such that:

τv≤k⋅τc\tau_v \le k \cdot \tau_c

Under no circumstance may the nominal shear stress exceed half the maximum shear strength:

τv≤0.5τc,max⁡\tau_v \le 0.5 \tau_{c,\max}

If τv>k⋅τc\tau_v > k \cdot \tau_c, the slab depth DD must be increased.


6. Continuous One-Way Slabs & Bending Moment Coefficients (Tables 12 & 13)

For continuous one-way slabs spanning over three or more approximately equal spans (spans differing by ≤15%\le 15\% of the longest span), IS 456 Clause 22.5.1 permits structural analysis using empirical moment and shear coefficients:

6.1 Bending Moment Coefficients (Table 12)

Mu=(αd⋅wud+αl⋅wul)⋅L2M_u = \left(\alpha_d \cdot w_{ud} + \alpha_l \cdot w_{ul}\right) \cdot L^2

Where wud=1.5wDLw_{ud} = 1.5 w_{DL} and wul=1.5wLLw_{ul} = 1.5 w_{LL}.

┌───────────────────────────────────────┬──────────────────────────┬──────────────────────────┐
│ Location along Continuous Slab        │ Dead Load Coeff (α_d)    │ Imposed Load Coeff (α_l) │
├───────────────────────────────────────┼──────────────────────────┼──────────────────────────┤
│ At near middle of end span            │ + 1/12                   │ + 1/10                   │
├───────────────────────────────────────┼──────────────────────────┼──────────────────────────┤
│ At middle of interior span            │ + 1/16                   │ + 1/12                   │
├───────────────────────────────────────┼──────────────────────────┼──────────────────────────┤
│ At support next to end support        │ - 1/10                   │ - 1/9                    │
│ (First Interior Support)              │                          │                          │
├───────────────────────────────────────┼──────────────────────────┼──────────────────────────┤
│ At other interior supports            │ - 1/12                   │ - 1/9                    │
└───────────────────────────────────────┴──────────────────────────┴──────────────────────────┘

6.2 Shear Force Coefficients (Table 13)

Vu=(βd⋅wud+βl⋅wul)⋅LV_u = \left(\beta_d \cdot w_{ud} + \beta_l \cdot w_{ul}\right) \cdot L
┌───────────────────────────────────────┬──────────────────────────┬──────────────────────────┐
│ Location along Continuous Slab        │ Dead Load Coeff (β_d)    │ Imposed Load Coeff (β_l) │
├───────────────────────────────────────┼──────────────────────────┼──────────────────────────┤
│ At end support                        │ 0.40                     │ 0.45                     │
├───────────────────────────────────────┼──────────────────────────┼──────────────────────────┤
│ At first interior support (outer side)│ 0.60                     │ 0.60                     │
├───────────────────────────────────────┼──────────────────────────┼──────────────────────────┤
│ At first interior support (inner side)│ 0.55                     │ 0.60                     │
├───────────────────────────────────────┼──────────────────────────┼──────────────────────────┤
│ At other interior supports            │ 0.50                     │ 0.60                     │
└───────────────────────────────────────┴──────────────────────────┴──────────────────────────┘

7. Engineering Diagrams & Detailing Anatomy

Diagram 1: One-Way Slab Behavior & 1-Meter Design Strip Idealization

The schematic below illustrates the aspect ratio threshold (Ly/Lx>2.0L_y / L_x > 2.0), cylindrical surface curvature, one-way load transfer to long edge beams, and the equivalent 1-meter wide strip beam model.

       ONE-WAY SLAB LOAD PATH & CYLINDRICAL CURVATURE
 ┌─────────────────────────────────────────────────────────────┐
 │  Long Edge Beam                               Long Edge Beam│
 │  ◄════════════════════════════════════════════════════════► │
 │  │                                                        │ │
 │  │      Load Transfer Arrows (Predominant Direction)      │ │
 │  │             ▲                              ▲           │ │
 │  │             │                              │           │ │
 │  │     ────────┼──────────────────────────────┼────────   │ │
 │  │             │  1-m Wide Design Strip       │           │ │
 │  │     ────────┼──────────────────────────────┼────────   │ │
 │  │             │                              │           │ │
 │  │             ▼                              ▼           │ │
 │  ◄════════════════════════════════════════════════════════► │
 └─────────────────────────────────────────────────────────────┘
One-Way Slab Behavior and Load Transfer

Diagram 2: One-Way Slab Reinforcement Detailing & Curtailment Rules

The schematic below illustrates the cross-sectional bar configuration, bottom main steel spacing limits (≤min⁡(3d,300 mm)\le \min(3d, 300\text{ mm})), top distribution steel spacing (≤min⁡(5d,450 mm)\le \min(5d, 450\text{ mm})), wall bearing anchorage, and 0.15L0.15 L bar cranking/curtailment.

       ONE-WAY SLAB REINFORCEMENT CROSS-SECTION & ELEVATION
 ┌─────────────────────────────────────────────────────────────┐
 │  Top Distribution Bars: s ≤ min(5d, 450 mm)                │
 │  ●       ●       ●       ●       ●       ●       ●       ●  │
 │  ═════════════════════════════════════════════════════════  │
 │  Bottom Main Bars: s ≤ min(3d, 300 mm); ϕ ≤ D/8            │
 │  ( )     ( )     ( )     ( )     ( )     ( )     ( )        │
 │  ─────────────────────────────────────────────────────────  │
 │  Clear Cover ≥ 20 mm (or 15 mm for bar diameter ≤ 12 mm)   │
 └─────────────────────────────────────────────────────────────┘
One-Way Slab Reinforcement Detailing and Curtailment

8. Step-by-Step Design Procedure for One-Way Slabs

                     ONE-WAY SLAB DESIGN WORKFLOW
                                   │
 ┌─────────────────────────────────┴─────────────────────────────────┐
 │ 1. Classify Slab: Verify Ly / Lx > 2.0 or 2-edge support.         │
 │ 2. Estimate Depth D: Based on deflection (L/d ≈ 25 - 30 for Fe415)│
 │    Compute effective depth d = D - c_nom - ϕ/2.                   │
 │ 3. Determine Effective Span (Leff): min(L0 + d, L0 + w).          │
 │ 4. Calculate Loads on 1-m Strip: Self-weight + Finishes + LL.     │
 │ 5. Compute Factored Mu & Vu: Mu = wu · Leff² / 8; Vu = wu · Leff/2│
 │ 6. Check Depth for Flexure: d ≥ √(Mu / (Q_lim · fck · 1000)).     │
 │ 7. Calculate Main Steel Ast & Spacing: s ≤ min(3d, 300 mm).       │
 │ 8. Design Distribution Steel: Ast,min = 0.12% b·D; s ≤ min(5d, 450)│
 │ 9. Check Shear Stress: τv = Vu / (b d) ≤ k · τc.                  │
 │ 10. Check Deflection: (L/d)_actual ≤ 20 · kt.                     │
 │ 11. Detail Reinforcement: Anchor ≥ 50% steel into supports (Ld/3).│
 └───────────────────────────────────────────────────────────────────┘

9. Pre-Calculated Solved Numerical Examples

Example 1: Comprehensive Design of a Simply Supported One-Way Slab

Problem Statement:
Design a simply supported reinforced concrete one-way roof slab spanning between two brick masonry walls having a clear span of Lx,clear=3.5 mL_{x,\text{clear}} = 3.5\text{ m}. The longer dimension of the room is Ly,clear=8.5 mL_{y,\text{clear}} = 8.5\text{ m}. The supporting walls are 230 mm230\text{ mm} thick.
Design data:

  • Live load (Imposed load) = 3.0 kN/m23.0\text{ kN/m}^2
  • Floor / Roof finish = 1.0 kN/m21.0\text{ kN/m}^2
  • Concrete grade = M20 (fck=20 MPaf_{ck} = 20\text{ MPa})
  • Steel grade = Fe 415 (fy=415 MPaf_y = 415\text{ MPa})
  • Unit weight of reinforced concrete γc=25 kN/m3\gamma_c = 25\text{ kN/m}^3

Solution:

Step 1: Check Aspect Ratio:

LyLx=8.53.5=2.43>2.0  ⟹  Designed as a One−Way Slab.\frac{L_y}{L_x} = \frac{8.5}{3.5} = 2.43 > 2.0 \implies \mathbf{Designed\ as\ a\ One-Way\ Slab.}

Step 2: Trial Depth Selection from Deflection Control: For simply supported slabs, basic L/d=20L/d = 20. For an assumed tension steel ratio pt≈0.35%p_t \approx 0.35\%, modification factor kt≈1.40k_t \approx 1.40:

Allowable Ld≈20×1.40=28  ⟹  dtrial=350028=125 mm\text{Allowable } \frac{L}{d} \approx 20 \times 1.40 = 28 \implies d_{\text{trial}} = \frac{3500}{28} = 125\text{ mm}

Adopting nominal clear cover cnom=20 mmc_{\text{nom}} = 20\text{ mm} and main bar diameter ϕ=10 mm\phi = 10\text{ mm}:

D=d+cnom+ϕ2=125+20+5=150 mmD = d + c_{\text{nom}} + \frac{\phi}{2} = 125 + 20 + 5 = 150\text{ mm}

Provided effective depth:

d=150−20−102=125.0 mmd = 150 - 20 - \frac{10}{2} = 125.0\text{ mm}

Step 3: Effective Span LeffL_{\text{eff}} (Clause 22.2a):

Leff=min⁡(L0+d,  L0+w)=min⁡(3.5+0.125,  3.5+0.230)=min⁡(3.625 m,  3.730 m)=3.625 mL_{\text{eff}} = \min(L_0 + d,\; L_0 + w) = \min(3.5 + 0.125,\; 3.5 + 0.230) = \min(3.625\text{ m},\; 3.730\text{ m}) = 3.625\text{ m}

Step 4: Load Calculation per 1-Meter Wide Strip (b=1000 mmb = 1000\text{ mm}):

  • Self-weight of slab: wDL=25×0.15×1.0=3.75 kN/mw_{DL} = 25 \times 0.15 \times 1.0 = 3.75\text{ kN/m}
  • Floor finishes: wFF=1.0×1.0=1.00 kN/mw_{FF} = 1.0 \times 1.0 = 1.00\text{ kN/m}
  • Imposed live load: wLL=3.0×1.0=3.00 kN/mw_{LL} = 3.0 \times 1.0 = 3.00\text{ kN/m}
  • Total service working load: w=3.75+1.00+3.00=7.75 kN/mw = 3.75 + 1.00 + 3.00 = 7.75\text{ kN/m}
  • Factored design load: wu=1.5×7.75=11.625 kN/mw_u = 1.5 \times 7.75 = 11.625\text{ kN/m}

Step 5: Factored Bending Moment & Shear Force:

Mu=wu⋅Leff28=11.625×3.62528=19.095 kNm=19.095×106 N⋅mmM_u = \frac{w_u \cdot L_{\text{eff}}^2}{8} = \frac{11.625 \times 3.625^2}{8} = 19.095\text{ kNm} = 19.095 \times 10^6\text{ N}\cdot\text{mm} Vu=wu⋅Leff2=11.625×3.6252=21.070 kNV_u = \frac{w_u \cdot L_{\text{eff}}}{2} = \frac{11.625 \times 3.625}{2} = 21.070\text{ kN}

Step 6: Check Depth for Flexure: For Fe 415, Qlim⁡=0.138Q_{\lim} = 0.138:

dmin⁡=MuQlim⁡fckb=19.095×1060.138×20×1000=6918.48=83.18 mm<125.0 mm  ⟹  SAFE.d_{\min} = \sqrt{\frac{M_u}{Q_{\lim} f_{ck} b}} = \sqrt{\frac{19.095 \times 10^6}{0.138 \times 20 \times 1000}} = \sqrt{6918.48} = 83.18\text{ mm} < 125.0\text{ mm} \implies \mathbf{SAFE}.

Step 7: Main Tension Reinforcement (AstA_{st}):

Ast=0.5×20415[1−1−4.59×19.095×10620×1000×1252]×1000×125A_{st} = \frac{0.5 \times 20}{415} \left[1 - \sqrt{1 - \frac{4.59 \times 19.095 \times 10^6}{20 \times 1000 \times 125^2}}\right] \times 1000 \times 125 Ast=0.024096×[1−1−0.28032]×125000=0.024096×[1−0.84834]×125000=456.98 mm2A_{st} = 0.024096 \times [1 - \sqrt{1 - 0.28032}] \times 125000 = 0.024096 \times [1 - 0.84834] \times 125000 = 456.98\text{ mm}^2

Minimum steel check (Clause 26.5.2.1):

Ast,min⁡=0.0012×1000×150=180.0 mm2<456.98 mm2  ⟹  OK.A_{st,\min} = 0.0012 \times 1000 \times 150 = 180.0\text{ mm}^2 < 456.98\text{ mm}^2 \implies \mathbf{OK}.

Spacing of 10 mmϕ10\text{ mm}\phi bars (ast=78.54 mm2a_{st} = 78.54\text{ mm}^2):

scalc=1000×78.54456.98=171.86 mms_{\text{calc}} = \frac{1000 \times 78.54}{456.98} = 171.86\text{ mm}

Maximum allowable spacing:

smax⁡=min⁡(3d,  300 mm)=min⁡(3×125=375,  300)=300 mms_{\max} = \min(3d,\; 300\text{ mm}) = \min(3 \times 125 = 375,\; 300) = 300\text{ mm}

Provide 10 mmϕ10\text{ mm}\phi bars @ 160 mm160\text{ mm} c/c:

Ast,prov=1000×78.54160=490.87 mm2(pt=490.871000×125×100=0.393%)A_{st,\text{prov}} = \frac{1000 \times 78.54}{160} = 490.87\text{ mm}^2 \quad \left(p_t = \frac{490.87}{1000 \times 125} \times 100 = 0.393\%\right)

Step 8: Distribution Reinforcement (HYSD 8 mmϕ8\text{ mm}\phi):

Ast,dist=Ast,min⁡=180.0 mm2A_{st,\text{dist}} = A_{st,\min} = 180.0\text{ mm}^2

Spacing of 8 mmϕ8\text{ mm}\phi bars (ast=50.27 mm2a_{st} = 50.27\text{ mm}^2):

sdist=1000×50.27180.0=279.25 mms_{\text{dist}} = \frac{1000 \times 50.27}{180.0} = 279.25\text{ mm}

Maximum allowable spacing:

smax⁡=min⁡(5d,  450 mm)=min⁡(5×125=625,  450)=450 mms_{\max} = \min(5d,\; 450\text{ mm}) = \min(5 \times 125 = 625,\; 450) = 450\text{ mm}

Provide 8 mmϕ8\text{ mm}\phi bars @ 250 mm250\text{ mm} c/c (Ast,dist=201.06 mm2A_{st,\text{dist}} = 201.06\text{ mm}^2).

Step 9: Check for Shear (Clause 40.2.1.1): Nominal shear stress:

τv=Vub⋅d=21.070×1031000×125=0.169 N/mm2\tau_v = \frac{V_u}{b \cdot d} = \frac{21.070 \times 10^3}{1000 \times 125} = 0.169\text{ N/mm}^2

For pt=0.393%p_t = 0.393\% in M20 concrete (Table 19):

τc=0.36+(0.48−0.360.50−0.25)(0.393−0.25)=0.36+0.0686=0.429 N/mm2\tau_c = 0.36 + \left(\frac{0.48 - 0.36}{0.50 - 0.25}\right) (0.393 - 0.25) = 0.36 + 0.0686 = 0.429\text{ N/mm}^2

Depth factor kk for D=150 mmD = 150\text{ mm} is k=1.30k = 1.30:

τc,slab=k⋅τc=1.30×0.429=0.558 N/mm2\tau_{c,\text{slab}} = k \cdot \tau_c = 1.30 \times 0.429 = 0.558\text{ N/mm}^2

Since τv=0.169 N/mm2≪τc,slab=0.558 N/mm2\tau_v = 0.169\text{ N/mm}^2 \ll \tau_{c,\text{slab}} = 0.558\text{ N/mm}^2, the slab is COMPLETELY SAFE IN SHEAR WITHOUT STIRRUPS.

Step 10: Check for Deflection Control (Clause 23.2.1):

fs=0.58fyAst,reqAst,prov=0.58×415×456.98490.87=224.08 N/mm2f_s = 0.58 f_y \frac{A_{st,\text{req}}}{A_{st,\text{prov}}} = 0.58 \times 415 \times \frac{456.98}{490.87} = 224.08\text{ N/mm}^2

For pt=0.393%p_t = 0.393\% and fs≈224 N/mm2f_s \approx 224\text{ N/mm}^2, Figure 4 gives kt=1.45k_t = 1.45:

(Ld)allowable=20×1.45=29.0\left(\frac{L}{d}\right)_{\text{allowable}} = 20 \times 1.45 = 29.0 (Ld)actual=3625125=29.00≤29.00  ⟹  SAFE IN DEFLECTION.\left(\frac{L}{d}\right)_{\text{actual}} = \frac{3625}{125} = 29.00 \le 29.00 \implies \mathbf{SAFE\ IN\ DEFLECTION}.

Example 2: Continuous One-Way Slab Analysis per IS 456 Table 12 & Table 13

Problem Statement:
A multi-panel floor system consists of continuous one-way slabs supported on parallel beams spaced at 3.6 m3.6\text{ m} clear centers over 3 equal spans. The slab carries a characteristic dead load (including self-weight and finishes) of g=4.5 kN/m2g = 4.5\text{ kN/m}^2 and an imposed live load of q=3.0 kN/m2q = 3.0\text{ kN/m}^2.
Using IS 456:2000 coefficients:

  1. Determine the factored design bending moment at the near middle of the end span, at the first interior support, and at the middle of the interior span.
  2. Determine the factored shear force at the outer face of the first interior support.

Solution:

Step 1: Factored Loads per 1-Meter Strip:

wud=1.5×4.5=6.75 kN/mw_{ud} = 1.5 \times 4.5 = 6.75\text{ kN/m} wul=1.5×3.0=4.50 kN/mw_{ul} = 1.5 \times 3.0 = 4.50\text{ kN/m}

Span L=3.6 m  ⟹  L2=12.96 m2L = 3.6\text{ m} \implies L^2 = 12.96\text{ m}^2.

Step 2: Factored Bending Moments (Table 12):

  1. Near Middle of End Span: Mu1=(112wud+110wul)L2=(6.7512+4.5010)×12.96=(0.5625+0.450)×12.96=+13.122 kNmM_{u1} = \left(\frac{1}{12} w_{ud} + \frac{1}{10} w_{ul}\right) L^2 = \left(\frac{6.75}{12} + \frac{4.50}{10}\right) \times 12.96 = (0.5625 + 0.450) \times 12.96 = \mathbf{+13.122\text{ kNm}}
  2. At First Interior Support: Mu2=−(110wud+19wul)L2=−(6.7510+4.509)×12.96=−(0.675+0.500)×12.96=−15.228 kNmM_{u2} = -\left(\frac{1}{10} w_{ud} + \frac{1}{9} w_{ul}\right) L^2 = -\left(\frac{6.75}{10} + \frac{4.50}{9}\right) \times 12.96 = -(0.675 + 0.500) \times 12.96 = \mathbf{-15.228\text{ kNm}}
  3. At Middle of Interior Span: Mu3=(116wud+112wul)L2=(6.7516+4.5012)×12.96=(0.421875+0.375)×12.96=+10.328 kNmM_{u3} = \left(\frac{1}{16} w_{ud} + \frac{1}{12} w_{ul}\right) L^2 = \left(\frac{6.75}{16} + \frac{4.50}{12}\right) \times 12.96 = (0.421875 + 0.375) \times 12.96 = \mathbf{+10.328\text{ kNm}}

Step 3: Factored Shear Force at First Interior Support (Table 13): At the outer side of the first interior support, βd=0.60\beta_d = 0.60 and βl=0.60\beta_l = 0.60:

Vu=(0.60wud+0.60wul)⋅L=0.60×(6.75+4.50)×3.6=0.60×11.25×3.6=24.300 kNV_u = (0.60 w_{ud} + 0.60 w_{ul}) \cdot L = 0.60 \times (6.75 + 4.50) \times 3.6 = 0.60 \times 11.25 \times 3.6 = \mathbf{24.300\text{ kN}}

Example 3: Cantilever Chhajja / Balcony Slab Design & Detailing

Problem Statement:
Design a cantilever chhajja (sunshade) slab having a clear projection of L0=1.2 mL_0 = 1.2\text{ m} from a 200 mm200\text{ mm} wide lintel beam. The live load is 1.5 kN/m21.5\text{ kN/m}^2, finish is 0.5 kN/m20.5\text{ kN/m}^2, and materials are concrete M20 (fck=20 MPaf_{ck} = 20\text{ MPa}) and steel Fe 415 (fy=415 MPaf_y = 415\text{ MPa}). To shed rainwater and reduce self-weight, the slab is tapered from Dsupp=120 mmD_{\text{supp}} = 120\text{ mm} at the root to Dtip=75 mmD_{\text{tip}} = 75\text{ mm} at the free tip. Clear cover is 20 mm20\text{ mm}.
Determine the required main top reinforcement and verify the section.

Solution:

Step 1: Effective Depth and Span: At the support:

d=Dsupp−cnom−ϕ2=120−20−4=96.0 mmd = D_{\text{supp}} - c_{\text{nom}} - \frac{\phi}{2} = 120 - 20 - 4 = 96.0\text{ mm}

Per Clause 22.2(c), for a cantilever built into a support:

Leff=L0+d2=1.20+0.0962=1.248 mL_{\text{eff}} = L_0 + \frac{d}{2} = 1.20 + \frac{0.096}{2} = 1.248\text{ m}

Step 2: Load Calculation (Average Thickness):

Davg=120+752=97.5 mm=0.0975 mD_{\text{avg}} = \frac{120 + 75}{2} = 97.5\text{ mm} = 0.0975\text{ m}
  • Self-weight: wDL=25×0.0975×1.0=2.4375 kN/mw_{DL} = 25 \times 0.0975 \times 1.0 = 2.4375\text{ kN/m}
  • Live load + Finish: wLL+FF=(1.5+0.5)×1.0=2.00 kN/mw_{LL+FF} = (1.5 + 0.5) \times 1.0 = 2.00\text{ kN/m}
  • Total service load: w=2.4375+2.00=4.4375 kN/mw = 2.4375 + 2.00 = 4.4375\text{ kN/m}
  • Factored load: wu=1.5×4.4375=6.65625 kN/mw_u = 1.5 \times 4.4375 = 6.65625\text{ kN/m}

Step 3: Factored Bending Moment & Shear:

Mu=wu⋅Leff22=6.65625×1.24822=5.184 kNm=5.184×106 N⋅mmM_u = \frac{w_u \cdot L_{\text{eff}}^2}{2} = \frac{6.65625 \times 1.248^2}{2} = 5.184\text{ kNm} = 5.184 \times 10^6\text{ N}\cdot\text{mm} Vu=wu⋅Leff=6.65625×1.248=8.307 kNV_u = w_u \cdot L_{\text{eff}} = 6.65625 \times 1.248 = 8.307\text{ kN}

Step 4: Main Reinforcement Calculation (Top Steel for Hogging):

Ast=0.5×20415[1−1−4.59×5.184×10620×1000×962]×1000×96=154.47 mm2A_{st} = \frac{0.5 \times 20}{415} \left[1 - \sqrt{1 - \frac{4.59 \times 5.184 \times 10^6}{20 \times 1000 \times 96^2}}\right] \times 1000 \times 96 = 154.47\text{ mm}^2

Minimum steel check at support (D=120 mmD = 120\text{ mm}):

Ast,min⁡=0.0012×1000×120=144.0 mm2<154.47 mm2  ⟹  OK.A_{st,\min} = 0.0012 \times 1000 \times 120 = 144.0\text{ mm}^2 < 154.47\text{ mm}^2 \implies \mathbf{OK}.

Spacing of 8 mmϕ8\text{ mm}\phi bars (ast=50.27 mm2a_{st} = 50.27\text{ mm}^2):

scalc=1000×50.27154.47=325.4 mms_{\text{calc}} = \frac{1000 \times 50.27}{154.47} = 325.4\text{ mm}

Maximum allowable spacing:

smax⁡=min⁡(3d,  300 mm)=min⁡(3×96=288,  300)=288 mms_{\max} = \min(3d,\; 300\text{ mm}) = \min(3 \times 96 = 288,\; 300) = 288\text{ mm}

Provide 8 mmϕ8\text{ mm}\phi bars @ 200 mm200\text{ mm} c/c as Top Main Steel (Ast,prov=251.33 mm2A_{st,\text{prov}} = 251.33\text{ mm}^2).
Anchorage: These top bars must be anchored into the lintel beam by at least full development length Ld=47ϕ=376 mmL_d = 47 \phi = 376\text{ mm}.


10. Engineering Misconceptions & Site Detailing Pitfalls

┌────────────────────────────────────────┬────────────────────────────────────────┬────────────────────────────────────────┐
│ Site Error / Detailing Defect          │ Engineering Consequence                │ IS 456:2000 Mandatory Remedy         │
├────────────────────────────────────────┼────────────────────────────────────────┼────────────────────────────────────────┤
│ Placing main reinforcement in the long │ Deflection and severe flexural         │ Main tension bars MUST always be       │
│ direction (Ly) instead of short (Lx)   │ cracking; slab collapses in flexure!   │ placed along the short span (Lx).      │
├────────────────────────────────────────┼────────────────────────────────────────┼────────────────────────────────────────┤
│ Omitting distribution steel in the     │ Uncontrolled thermal and shrinkage     │ Provide at least 0.12% bD (HYSD)       │
│ longitudinal direction                 │ cracks tear across the slab width.     │ distribution steel at s ≤ min(5d, 450).│
├────────────────────────────────────────┼────────────────────────────────────────┼────────────────────────────────────────┤
│ Walking on cantilever top rebar during │ Top steel gets pushed to the bottom;   │ Use rigid steel chair spacers to       │
│ concreting, displacing it downward     │ cantilever collapses upon form removal!│ preserve effective depth d at the top. │
├────────────────────────────────────────┼────────────────────────────────────────┼────────────────────────────────────────┤
│ Specifying shear stirrups in thin      │ Extreme bar crowding and honeycomb;   │ Slabs do not use shear stirrups;       │
│ one-way floor slabs                    │ impossible to pour and vibrate.        │ size depth so τv ≤ k · τc.             │
└────────────────────────────────────────┴────────────────────────────────────────┴────────────────────────────────────────┘

11. Comparative Analysis: One-Way Slabs vs Two-Way Slabs

Feature One-Way Slab Two-Way Slab
Aspect Ratio Condition Ly/Lx>2.0L_y / L_x > 2.0 (or supported on 2 edges) Ly/Lx≤2.0L_y / L_x \le 2.0 (supported on 4 edges)
Deflection / Curvature Shape Cylindrical curvature (bends along LxL_x) Dishing / Saucer curvature (bends along both LxL_x and LyL_y)
Load Sharing Mechanism >94%>94\% load transferred along short span Load shared between both pairs of beams per Rankine-Grashoff / Annex D
Design Model 1-meter wide strip beam across LxL_x Plate bending / Strip division (Middle & Edge strips)
Primary Reinforcement Single layer along short span LxL_x Two orthogonal layers of main steel (LxL_x below, LyL_y above)
Transverse Reinforcement Nominal distribution steel (≥0.12%bD\ge 0.12\% b D) Full flexural design steel in both directions
Corner Torsion Reinforcement Not required Mandatory at discontinuous corners (0.75Astx0.75 A_{stx} in 4 layers)
Typical Thickness Thicker (Span/25 to Span/30\text{Span} / 25 \text{ to } \text{Span} / 30) Thinner (Span/32 to Span/40\text{Span} / 32 \text{ to } \text{Span} / 40)

12. Competitive Exam Traps & High-Yield Takeaways

[!CAUTION] GATE / ESE High-Yield Trap Checklist:

  1. Grillage Analogy 4th-Power Law: Remember that load shared varies inversely with the 4th power of span: wx/wy=(Ly/Lx)4w_x / w_y = (L_y / L_x)^4. At Ly/Lx=2L_y / L_x = 2, exactly 16/1716/17 (94.1%94.1\%) load is carried in the short direction.
  2. Effective Depth of Cantilever: For a cantilever built into a wall, Leff=L0+d/2L_{\text{eff}} = L_0 + d/2. For a cantilever forming the continuation of a beam, Leff=L0+w/2L_{\text{eff}} = L_0 + w/2.
  3. Minimum Steel Gross vs Effective Depth: Ast,min⁡=0.12%⋅b⋅DA_{st,\min} = 0.12\% \cdot b \cdot D (uses gross depth DD, not effective depth dd!).
  4. Bar Diameter Limit: ϕ≤D/8\phi \le D / 8. For a 120 mm120\text{ mm} slab, max bar size is 15 mm15\text{ mm} (never use 16 mm16\text{ mm}!).
  5. Maximum Spacing Limits:
    • Main steel: min⁡(3d,300 mm)\min(3d, 300\text{ mm}).
    • Distribution steel: min⁡(5d,450 mm)\min(5d, 450\text{ mm}).
  6. Shear Depth Factor kk: For D≤150 mmD \le 150\text{ mm}, k=1.30k = 1.30. For D≥300 mmD \ge 300\text{ mm}, k=1.00k = 1.00. Stirrups are never used in slabs.
  7. Support Anchorage Rule: At least 50%50\% of positive flexural reinforcement must extend into supports by ≥Ld/3\ge L_d / 3 (Clause 26.2.3.3).

13. Practice Questions & Exercises

Question 1 (GATE CE)

A reinforced concrete slab of total depth 160 mm160\text{ mm} is reinforced with high yield strength deformed bars (Fe 415). The minimum area of reinforcement per meter width and the maximum permissible diameter of the reinforcing bar are respectively:

  • (A) 192 mm2192\text{ mm}^2 and 20 mm20\text{ mm}
  • (B) 240 mm2240\text{ mm}^2 and 20 mm20\text{ mm}
  • (C) 192 mm2192\text{ mm}^2 and 16 mm16\text{ mm}
  • (D) 240 mm2240\text{ mm}^2 and 16 mm16\text{ mm}

Answer: (A)
Explanation:
For Fe 415, Ast,min⁡=0.12%⋅b⋅D=0.12100×1000×160=192 mm2A_{st,\min} = 0.12\% \cdot b \cdot D = \frac{0.12}{100} \times 1000 \times 160 = 192\text{ mm}^2.
Maximum bar diameter ϕmax⁡=D8=1608=20 mm\phi_{\max} = \frac{D}{8} = \frac{160}{8} = 20\text{ mm}.


Question 2 (UPSC ESE)

In a simply supported one-way slab of effective depth 120 mm120\text{ mm}, the maximum clear spacing permitted by IS 456:2000 for the main flexural reinforcement and secondary distribution reinforcement respectively are:

  • (A) 300 mm300\text{ mm} and 450 mm450\text{ mm}
  • (B) 360 mm360\text{ mm} and 600 mm600\text{ mm}
  • (C) 300 mm300\text{ mm} and 300 mm300\text{ mm}
  • (D) 250 mm250\text{ mm} and 350 mm350\text{ mm}

Answer: (A)
Explanation:
Main reinforcement: smax⁡=min⁡(3d,300 mm)=min⁡(3×120=360,300)=300 mms_{\max} = \min(3d, 300\text{ mm}) = \min(3 \times 120 = 360, 300) = 300\text{ mm}.
Distribution reinforcement: smax⁡=min⁡(5d,450 mm)=min⁡(5×120=600,450)=450 mms_{\max} = \min(5d, 450\text{ mm}) = \min(5 \times 120 = 600, 450) = 450\text{ mm}.


Question 3 (SSC JE)

Per IS 456:2000, what is the value of the depth factor kk used to enhance the design shear strength τc\tau_c of a reinforced concrete slab of overall depth 140 mm140\text{ mm}?

  • (A) 1.001.00
  • (B) 1.151.15
  • (C) 1.201.20
  • (D) 1.301.30

Answer: (D)
Explanation:
Per Clause 40.2.1.1, for slabs of overall depth D≤150 mmD \le 150\text{ mm}, the depth factor k=1.30k = 1.30.

About this page’s source
Topic ID
RCC-05-01 (from metadata/sync_topic.py MAPPINGS)
Source file
notes/reinforced_cement_concrete/05_design_of_slabs/01_one_way_slabs.md
Presentation changes
  • Leading title heading and bold Key: value metadata lines shown in the page header instead of the body
  • Correction C-057 applied: Interpolated τ_c 0.428 → 0.429 N/mm²
  • Correction C-058 applied: Slab shear strength k·τ_c 0.556 → 0.558 N/mm²
  • Correction C-059 applied: Carried value 0.556 → 0.558 N/mm² in the shear conclusion
  • Correction C-060 applied: Steel service stress f_s 224.53 → 224.08 N/mm²
  • Correction C-061 applied: Chart entry value f_s ≈ 225 → ≈ 224 N/mm²
  • Correction C-062 applied: Hogging steel A_st 154.73 → 154.47 mm²
  • Correction C-063 applied: Carried value A_st 154.73 → 154.47 mm² in the minimum-steel check
  • Correction C-064 applied: Calculated spacing 324.8 → 325.4 mm